A 100GBASE-SR4 fault usually needs a lane-by-lane diagnosis rather than a single power reading. First confirm whether the port is native 100G or a 4x25G breakout; the same MPO cable behaves differently depending on the host configuration. For breakout, each lane should map to one 25G port, and an unexpected lane order is often a polarity mismatch. For SR4 on a parallel MPO, Type B crossover polarity is the common default, so a straight-through cable can make lanes appear swapped even if total power looks fine. After that, read per-lane Rx power via DOM on both ends. A typical baseline is around -5 to -7 dBm on a short OM4 link; one lane sitting near -10 dBm or below, while the others are normal, points to a dirty connector, a bent fiber, or a misaligned MPO ferrule. Cleaning both MPO ends and recleaning before reinsertion often fixes the marginal lane. If all four lanes look normal but errors persist, check the host breakout mapping and the firmware on the module. Which DOM field does your switch expose for per-lane Rx on 100G SR4 modules?